Transfer Switch Gameplan - Thoughts?

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
You can do whatever you want, but being a Master Electrician with close to 40 years of experience recommend that you don’t do this and install the correct equipment to make this work
So we go back to the original question. What chain of events that present a hazard do you base this position off of?

I see it as 1) deferring to what you've been instructed to do, or 2) you're seeing a hazard that you're failing to share.

I will continue to ask this question not to be redundant, but because I want to know what hazard possibilities arise out of the most skewed swiss cheese model. When fed by utility, the neutral floating is big danger. The truck and its GFI protections don't share these sets of risk factors. Furthermore if the truck does become earthed, GFI kicks in. So take as much time as you need, utilizing whatever resources you have available to illustrate what conditions must align to present a hazard. Thanks
Sponsored

 
OP
OP
Kodiak

Kodiak

Well-known member
Joined
Apr 27, 2022
Threads
46
Messages
2,303
Reaction score
3,131
Location
Virginia
Vehicles
2022 F-150 Lariat PB 7.2k, 4x4 502a Atlas Blue BAP
Bummer. I just had the electrician swap out my old subpanel (transfer switch) for a new Generac 6852 and it did not work. :(

Everything in the house is working as it should but if I switch to Gernerator the trucks GFCI trips.

We hooked it up with none of the 8 breakers active and the truck works fine. Once we flip anyone of the 8 breakers it trips. We tried each one, one at a time. Truck is in Generator Mode with no circuits and as soon as one get flipped to on, the GFCI on the truck trips.

They went over everything and said they wired it as per the Generac instructions but no good.

The main guy is coming back on Monday to look over everything. Anyone have any ideas or directions I can go with the setup I have. Any ideas to try out? Thanks in advance for any replies.
 

GIjoe

Well-known member
First Name
Joe
Joined
May 20, 2022
Threads
22
Messages
326
Reaction score
229
Location
Ohio
Vehicles
2013 f250
Bummer. I just had the electrician swap out my old subpanel (transfer switch) for a new Generac 6852 and it did not work. :(

Everything in the house is working as it should but if I switch to Gernerator the trucks GFCI trips.

We hooked it up with none of the 8 breakers active and the truck works fine. Once we flip anyone of the 8 breakers it trips. We tried each one, one at a time. Truck is in Generator Mode with no circuits and as soon as one get flipped to on, the GFCI on the truck trips.

They went over everything and said they wired it as per the Generac instructions but no good.

The main guy is coming back on Monday to look over everything. Anyone have any ideas or directions I can go with the setup I have. Any ideas to try out? Thanks in advance for any replies.
Yes- read this whole thread or go back a page where one poster summarized the issues
 

Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
Bummer. I just had the electrician swap out my old subpanel (transfer switch) for a new Generac 6852 and it did not work. :(

Everything in the house is working as it should but if I switch to Gernerator the trucks GFCI trips.

We hooked it up with none of the 8 breakers active and the truck works fine. Once we flip anyone of the 8 breakers it trips. We tried each one, one at a time. Truck is in Generator Mode with no circuits and as soon as one get flipped to on, the GFCI on the truck trips.

They went over everything and said they wired it as per the Generac instructions but no good.

The main guy is coming back on Monday to look over everything. Anyone have any ideas or directions I can go with the setup I have. Any ideas to try out? Thanks in advance for any replies.
It sucks for sure. It should work as several on this forum are using it without problems. I know my Eaton panel CPL112G3 can be used with generator that have bonded neutral or un-bonded neutral. I think there is a small difference in the install.
 

Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
Bummer. I just had the electrician swap out my old subpanel (transfer switch) for a new Generac 6852 and it did not work. :(

Everything in the house is working as it should but if I switch to Gernerator the trucks GFCI trips.

We hooked it up with none of the 8 breakers active and the truck works fine. Once we flip anyone of the 8 breakers it trips. We tried each one, one at a time. Truck is in Generator Mode with no circuits and as soon as one get flipped to on, the GFCI on the truck trips.

They went over everything and said they wired it as per the Generac instructions but no good.

The main guy is coming back on Monday to look over everything. Anyone have any ideas or directions I can go with the setup I have. Any ideas to try out? Thanks in advance for any replies.
One thing I could think of is, the person did not move all the circuits properly. All the neutrals of the relocated circuits have to be relocated to your Generac panel.
 

Sponsored

OP
OP
Kodiak

Kodiak

Well-known member
Joined
Apr 27, 2022
Threads
46
Messages
2,303
Reaction score
3,131
Location
Virginia
Vehicles
2022 F-150 Lariat PB 7.2k, 4x4 502a Atlas Blue BAP
One thing I could think of is, the person did not move all the circuits properly. All the neutrals of the relocated circuits have to be relocated to your Generac panel.
Thanks, I did have him move 2 new circuits over. I had 6 in the Eaton but had room for 8 in the Generac. I made note of this and will show it to the guy when he comes back.
 

Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
Thanks, I did have him move 2 new circuits over. I had 6 in the Eaton but had room for 8 in the Generac. I made note of this and will show it to the guy when he comes back.
I don't know the type of breaker that you used in the Generac but in my Eaton I can put either 6 regular breakers (6x circuits) or 6x twin breakers which are 12 different circuits.
 

DMuiser

Well-known member
First Name
Daniel
Joined
Dec 22, 2021
Threads
9
Messages
107
Reaction score
103
Location
Prince Edward Island, Canada
Vehicles
F150
So we go back to the original question. What chain of events that present a hazard do you base this position off of?

I see it as 1) deferring to what you've been instructed to do, or 2) you're seeing a hazard that you're failing to share.

I will continue to ask this question not to be redundant, but because I want to know what hazard possibilities arise out of the most skewed swiss cheese model. When fed by utility, the neutral floating is big danger. The truck and its GFI protections don't share these sets of risk factors. Furthermore if the truck does become earthed, GFI kicks in. So take as much time as you need, utilizing whatever resources you have available to illustrate what conditions must align to present a hazard. Thanks
1) All of this is over my head and using a dogbone interests me but according to electricians on here it is “unsafe”. I would like to know exactly what is unsafe about it so I can make an informed decision weather or not to go down that route. Only Answer I read so far is that the dog one might get used for something else that it shouldn’t with the ground cut.

2) I already have a generlink which allows me to power whole panel of my house, do we think this dogbone technique would work with it? Unfortunately cannot test a generlink until the power goes out
 
OP
OP
Kodiak

Kodiak

Well-known member
Joined
Apr 27, 2022
Threads
46
Messages
2,303
Reaction score
3,131
Location
Virginia
Vehicles
2022 F-150 Lariat PB 7.2k, 4x4 502a Atlas Blue BAP
I don't know the type of breaker that you used in the Generac but in my Eaton I can put either 6 regular breakers (6x circuits) or 6x twin breakers which are 12 different circuits.
The Generac came with 6 Siemans breakers (15 & 20) and it had one double breaker (30) in it. We took out the double breaker and added in the 2 new Siemans breakers. That gave us 8 single breakers total. A mix of 15s and 20s. The Generac instructions said it could take 8 or 10 but I do not know how it could get to 10.

With that said I made sure to go buy the exact breaker (Siemans) that the Generac came with.
 

SouthernGuy

Active member
First Name
Sam
Joined
Dec 17, 2021
Threads
2
Messages
41
Reaction score
51
Location
Alabama
Vehicles
'21 Lariat Powerboost, 7.2K PPoB
Occupation
Retired
I do not know how it could get to 10
You take out a single breaker and put in a tandem breaker. It turns one slot into 2 breakers. I used a couple of these to have 10 circuits in my Generac transfer switch.
Ford F-150 Transfer Switch Gameplan - Thoughts? 1696674656962
 

Sponsored


Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
So we go back to the original question. What chain of events that present a hazard do you base this position off of?

I see it as 1) deferring to what you've been instructed to do, or 2) you're seeing a hazard that you're failing to share.

I will continue to ask this question not to be redundant, but because I want to know what hazard possibilities arise out of the most skewed swiss cheese model. When fed by utility, the neutral floating is big danger. The truck and its GFI protections don't share these sets of risk factors. Furthermore if the truck does become earthed, GFI kicks in. So take as much time as you need, utilizing whatever resources you have available to illustrate what conditions must align to present a hazard. Thanks
With the ground removed from the truck the normal power grounding wires can become alive. It won’t trip anything until the circuit is complete. Which could be A person completing the circuit. It should trip the gfi.
my question for you is why take a shortcut when the equipment to make the truck as safe as possible and is proscribed by the National Electrical Code is available at a reasonable price. Most states adhere to the NEC, but some, like my own, have a more stringent set of standards, based on the NEC. To protect life and property. It’s not a set of standards you only comply with when you feel like it.
When I do an electrical job I am responsible for the job for my whole life. I will never advocate to take a shortcut outside of the NEC.
 

Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
1) All of this is over my head and using a dogbone interests me but according to electricians on here it is “unsafe”. I would like to know exactly what is unsafe about it so I can make an informed decision weather or not to go down that route. Only Answer I read so far is that the dog one might get used for something else that it shouldn’t with the ground cut.

2) I already have a generlink which allows me to power whole panel of my house, do we think this dogbone technique would work with it? Unfortunately cannot test a generlink until the power goes out
1)https://www.electricgeneratorsdirect.com/manuals/generac-b156120beb66561e5ab2f46e3773a9e6.pdf This is the link for the Generac panel not Generlink. If you look into it, never they say to lift a ground or float it. At the opposite they mention to ensure everything is connected properly. Now if something was to happen(someone get electrified, burn your house, damage some of your equipment) because you choose the route of lifting the ground, how would you feel? I just try to imagine the defense of anyone going that route... "well mr. the judge I red it on the internet it was OK and safe to do it".

2) You could turn off your main breaker to run the test.
 

Davexxxx

Well-known member
Joined
Mar 25, 2023
Threads
82
Messages
1,822
Reaction score
1,912
Location
MO
Vehicles
2023 PB 501a 4x4 short bed 7.2KW. PL=1658lbs.
When I do an electrical job I am responsible for the job for my whole life. I will never advocate to take a shortcut outside of the NEC.
This is a perfectly reasonable position for any licensed professional. I can relate.

However, it doesn't preclude you from discussing pros and cons of alternatives, short of offering advice, on tasks you aren't paid to do.

~This is better and here is why. That would work too but at your own risk and be aware of X, X, and X possibilities.~ carries no liability, if you haven't been paid for it.

If I was building new, or even had a place where it could be reasonably easy to do, I'd go the full transfer switch route but neither is true for me. Service panel at one end, truck on the other and a full length finished basement ceiling in between.

So, I need a workaround.

One of course, is extension cords strung everywhere to individual appliances, which carry their own risks.

What I have, is one switched, dedicated (nothing else on it) 20a receptacle circuit, within reach of the truck. It has a 20A rated receptacle in it and is served by an existing sub panel in the basement. It's breaker, is of the GFI type.

I made my own "dogbone" with 10 ga wire, leaving the ground and L2, disconnected at the truck end and connected it through a 20A rated 10ga cord. I used the 30a on the truck, in an effort to avoid the suicide cord situation, counting on the house breaker to limit overdraw.

Turned the power off at the main and the main and all other circuits at the sub panel (which are not supposed to be NG bonded). Truck still tripped instantly when the switch was energized.

What I'll try next, is replace the GFI breaker with a standard, non GFI breaker. Don't get lost in the codes on that part. My area doesn't require them on existing structures. I had the previous owner install it as a condition of the sale. There is no inspection here of existing structures.

I respect your experience and license but seeing the "truck as the utility" is a compelling argument. The truck is protected internally and the house has it's own ground.

If the plug at the truck is in place, before and after generator mode is engaged, where is the risk?
 
OP
OP
Kodiak

Kodiak

Well-known member
Joined
Apr 27, 2022
Threads
46
Messages
2,303
Reaction score
3,131
Location
Virginia
Vehicles
2022 F-150 Lariat PB 7.2k, 4x4 502a Atlas Blue BAP
You take out a single breaker and put in a tandem breaker. It turns one slot into 2 breakers. I used a couple of these to have 10 circuits in my Generac transfer switch.
1696674656962.png
HA! Thanks for the picture. I did know this was even a thing. :)
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
This is a perfectly reasonable position for any licensed professional. I can relate.

However, it doesn't preclude you from discussing pros and cons of alternatives, short of offering advice, on tasks you aren't paid to do.

~This is better and here is why. That would work too but at your own risk and be aware of X, X, and X possibilities.~ carries no liability, if you haven't been paid for it.

If I was building new, or even had a place where it could be reasonably easy to do, I'd go the full transfer switch route but neither is true for me. Service panel at one end, truck on the other and a full length finished basement ceiling in between.

So, I need a workaround.

One of course, is extension cords strung everywhere to individual appliances, which carry their own risks.

What I have, is one switched, dedicated (nothing else on it) 20a receptacle circuit, within reach of the truck. It has a 20A rated receptacle in it and is served by an existing sub panel in the basement. It's breaker, is of the GFI type.

I made my own "dogbone" with 10 ga wire, leaving the ground and L2, disconnected at the truck end and connected it through a 20A rated 10ga cord. I used the 30a on the truck, in an effort to avoid the suicide cord situation, counting on the house breaker to limit overdraw.

Turned the power off at the main and the main and all other circuits at the sub panel (which are not supposed to be NG bonded). Truck still tripped instantly when the switch was energized.

What I'll try next, is replace the GFI breaker with a standard, non GFI breaker. Don't get lost in the codes on that part. My area doesn't require them on existing structures. I had the previous owner install it as a condition of the sale. There is no inspection here of existing structures.

I respect your experience and license but seeing the "truck as the utility" is a compelling argument. The truck is protected internally and the house has it's own ground.

If the plug at the truck is in place, before and after generator mode is engaged, where is the risk?
[/QUOTE
There’s no ground!