That's where being a layman gets me into trouble. I read that and don't think connecting a home can qualify.let me throw some more mud on this discussion. Do you each consider the PB to be a vehicle mounted generator? And if so would 250.34 of the nec then apply? Does that change the discussion?
The frame of a vehicle shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by a generator located on this vehicle under the following conditions:
- The frame of the generator is bonded to the vehicle frame, and
- The generator supplies only equipment located on the vehicle or cord-and-plug-connected equipment through receptacles mounted on the vehicle, or both equipment located on the vehicle and cord-and-plug-connected equipment through receptacles mounted on the vehicle or on the generator, and
- The normally non-current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
I see a home connected to a PB as not meeting #2. We're connecting to downstream receptacles with their own GFCI, bonding, and grounding points. This is why I keep sounding hinky about the PB, or portable generator not needing an earth ground.
That's also the root of the issue - If we were connecting "equipment" directly to the genset plugs there would be no issue. We aren't. Layman read: This applies to devices on the jobsite, even devices directly connected from onside a home. but not when backfeeding home panels.
Again, WTH do I know.