Hullguy
- First Name
- Jim
- Joined
- Oct 14, 2020
- Threads
- 7
- Messages
- 488
- Reaction score
- 468
- Location
- Weymouth, MA
- Vehicles
- 2013 F150 FX 4
- Occupation
- Retired Union Electrician
Cheaper and safer to buy the correct equipment to transfer power than go in and try to modify the trucks grounding!Your 7.2kW generator has all the power you need to run most houses including an A/C unit. So what do you need to be safe and comply with the NEC? 1- an interlock between the input breaker and the outside line input breaker (Square D makes a manual one); 2- A male input plug box, weather tight; 3- A 240VAC 30Amp 4-wire extension cable (Home Depot carries them)(do not use a male-male cable); 4- the input system must be 4-wire: 2 hot wires, 1 neutral wire and 1 ground wire. The current problem you'll run into is that the PB generator is set up as a bonded neutral-ground in the truck. When the truck sense the neutral ground bond inside your hosue it'll shut down the generator. This is why many talk of a neutral switching breaker & panel (usually a smaller emergency panel). How ever you might talk to Ford (as I have done) and ask them for a method to convert your truck to a floating neutral generator. That fixes the problem of the truck shutting down the generator. Some have spoken of opening the ground between the truck and the house and that will work. But... it's a bad idea and doesn't meet the NEC.