You'd have to verify w/ a scope. It's not a simple task to both clean up the wave and ensure proper frequency.
Sponsored

 

ReverendQ

Well-known member
First Name
Kevin
Joined
Mar 26, 2023
Threads
18
Messages
640
Reaction score
727
Location
SoCal
Website
www.linkedin.com
Vehicles
2023 F150 XLT PowerBoost 302A Avalanche BAP
Occupation
Engineer
@HammaMan I’m certainly no expert and very capable of getting things wrong. I’m currently using pure sine wave UPS units for the better electronics.
Something like this:

IMG_0159.jpg
I used to work in UPS as a Test Engineer, but much larger units i.e. 750KVA plus. The rectify utility AC-to DC battery bus - back to AC for loads process usually produced a dirtier wave. And consider the load switching may be causing noise on the source. Really, you have to see it to know if it cleans it. O-Scope time.
 

Samson16

Well-known member
First Name
Kyle
Joined
Mar 24, 2023
Threads
18
Messages
3,622
Reaction score
3,587
Location
Orlando, FL.
Vehicles
'22 F-150 XLT Powerboost Super Crew 4x4
Occupation
Aviation systems
I used to work in UPS as a Test Engineer, but much larger units i.e. 750KVA plus. The rectify utility AC-to DC battery bus - back to AC for loads process usually produced a dirtier wave. And consider the load switching may be causing noise on the source. Really, you have to see it to know if it cleans it. O-Scope time.
I do have an O-scope. I’m thinking my non inverter generator gets even trashier when the 4.5 ton compressor kicks on. I use a MicroAire easy start which helps but I bet the frequency and voltage struggle momentarily lol. I’ll see if I can capture it
 

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
Interestingly, after being critical of the Generac Manual transfer switch box, I ended up installing one in my house. Reason: I needed more breaker slots than the main panel I installed years ago. The Generac Panel gave me the 10 more slots I needed without having to buy and install another main panel. Observation: when you power up the Generator Source and then switch to it, it trips the trucks ground circuit dumping the generator. It then restarts and runs just fine as the alternate power source. It's just really odd that the act of transferring power trips it. I'll try it from both a dead utility condition and a manual shift to see if it still trips the truck.
 
Last edited:

rdmjr

New member
First Name
Ron
Joined
Dec 22, 2024
Threads
0
Messages
1
Reaction score
0
Location
PA
Vehicles
2024 F150 Powerboost
Occupation
Engineer
I am having a similar issue. When I have the 50A transfer panel supply breaker in the main panel turned on when I power the generator I get power shown on the orange panel light, but the generator GFCI trips out when I hit the transfer button. This is with all the transfer panel breakers turned off.

If I turn off the 50A supply breaker in the main panel the transfer occurs properly.

After I have the generator supplying power to the panel, I can turn the 50A supply breaker in the main panel back on and things continue to run properly with the green utility light now illuminated. When I press the transfer button to go back to utility power the transfer happens properly, but the generator GFCI trips out again.

I installed the Generac 9854 according to the instructions. I moved all the neutrals, and I do not have a connection between the N and G bus bar in the transfer switch panel. I have the ground and the neutral cables from the individual transfer switch bus bars going to the main panel on separate cables to the G/N bus bar. All my circuit grounds are still wired to my main panel, I only moved the hot and neutral wires.

I do not have any additional grounding rods added, I depend on ground in the cable connector to connect back to my main panel ground system.

Has anyone had a similar experience, and how was it resolved?
 

Sponsored

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
I believe that tripping occurs because the actual switch in the panel is a make before break type switch. Thus the truck's GFCI senses the additional neutral-ground bond and trips. Then, since they are in fact then broken, it comes back on line and operates fine. There's nothing wrong with any of your wiring, the issue lies in the switch itself.
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
I am having a similar issue. When I have the 50A transfer panel supply breaker in the main panel turned on when I power the generator I get power shown on the orange panel light, but the generator GFCI trips out when I hit the transfer button. This is with all the transfer panel breakers turned off.

If I turn off the 50A supply breaker in the main panel the transfer occurs properly.

After I have the generator supplying power to the panel, I can turn the 50A supply breaker in the main panel back on and things continue to run properly with the green utility light now illuminated. When I press the transfer button to go back to utility power the transfer happens properly, but the generator GFCI trips out again.

I installed the Generac 9854 according to the instructions. I moved all the neutrals, and I do not have a connection between the N and G bus bar in the transfer switch panel. I have the ground and the neutral cables from the individual transfer switch bus bars going to the main panel on separate cables to the G/N bus bar. All my circuit grounds are still wired to my main panel, I only moved the hot and neutral wires.

I do not have any additional grounding rods added, I depend on ground in the cable connector to connect back to my main panel ground system.

Has anyone had a similar experience, and how was it resolved?
That’s how mine works as well. I don’t believe there is a work around.
 

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
I had one of those installed in my panel. It worked well except the Truck's Ground Fault Sensor detects the panel's neutral ground bond and shuts down its generator. If you cannot open up that neutral ground bonding, you cannot run the Truck's generator on the house. At least until Ford gets around their refusal to remove or deactivate the Truck's programming that shuts down the generator when it senses the house's bond.