I see now - each inverter controls 120V and one side of the split phase 240 - so they are not in parallel. Cool.

You have not shown any neutral or ground connections to the mains or PB. I would look carefully into the inverter specs regarding bonding (ie neutral to ground connections). The PB is internally bonded and cannot be disconnected - usually main power is also neutral-ground bonded, which would lead to GFI trips in the PB. Do the parallel Victrons somehow ensure all power pulled from mains or PB is always balanced between the 2 x 120V split legs? Cant see how this works...
Sponsored

 

powerboatr

Well-known member
First Name
Robert
Joined
May 9, 2022
Threads
173
Messages
4,343
Reaction score
5,427
Location
North East Texas, Piney Woods
Vehicles
2024 F250 King Ranch Chrome
Occupation
Retired Navy Senior Chief
Since owning my 2023 7.2kW PowerBoost, we have used it's incredible generator/inverter capability to power critical circuits in our house during multiple grid failures. Critical circuits include, refrigerator/freezers, furnace, security system, well pump and strategic lights and outlets. It has been flawless. The only problem has been grid failure when I am not home with the truck...duh! Soooo...

Of course, I could install a standby generator but that seems soooo 2010's. I have decided to build a battery backup system, with some twists.

System Requirements:

  • Easily power the critical circuits currently powered by PowerBoost.
  • Enough stored energy ( batteries ) to power critical circuits for three days.
  • Expandable energy storage
  • Include automatic transfer function <20ms - UPS mode - in grid down.
  • Include automatic transfer function to generator source ( PowerBoost ) to recharge batteries and power circuits

Simply put, I am building a home UPS system that will automatically recognize when either grid or PowerBoost is available to recharge batteries and power critical circuits. We rarely have grid failures over three days and with this system the PowerBoost should easily keep us going for weeks

Still in the planning stage, but very close to build stage. It should be fun!

Yes, of course, this offgrid design is most often used in solar or yacht systems, but I think the PowerBoost is the perfect secondary power source.

Here is a drawing of what I have come up with so far. I am NOT an electrician - obviously.

Oh, almost forgot! I did confirm a 30% Clean Energy tax credit for the system that can be carried forward until 2035. Cool!

backup-v3-5-to-scale.jpg
Tell us more on extending tax credits
 
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
I see now - each inverter controls 120V and one side of the split phase 240 - so they are not in parallel. Cool.

You have not shown any neutral or ground connections to the mains or PB. I would look carefully into the inverter specs regarding bonding (ie neutral to ground connections). The PB is internally bonded and cannot be disconnected - usually main power is also neutral-ground bonded, which would lead to GFI trips in the PB. Do the parallel Victrons somehow ensure all power pulled from mains or PB is always balanced between the 2 x 120V split legs? Cant see how this works...

Very good questions!! I am still studying and trying to learn but am assured by those who would be programming the units and drawing the final plans that it will work. The neutral/ground connections definitely elude me and why I did not include them in my drawing other than in sub panel. When I have final drawings I will definitely share.

Thanks for asking!
 

Sponsored

OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired

Mszczewski

Well-known member
First Name
Mark
Joined
Sep 26, 2022
Threads
6
Messages
136
Reaction score
169
Location
Milwaukee, WI
Vehicles
21 F-150 Lariat Powerboost
Very interest to see how this works out. If it goes well for you I might be right behind you.
 

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
I have looked thru the section on AC in that book. They always seem to refer to paralleling at the 120VAC level. However when you are thinking of 240VAC the paralleling is different in that you are going above and below the neutral level. They just don't address this aspect. That's why I'm uneasy with the idea. I think its a good thing to pursue as it then opens up the entirety of running a house set up with utility wiring and the full 7.2kW of the PB.
 

Sponsored


ReverendQ

Well-known member
First Name
Kevin
Joined
Mar 26, 2023
Threads
18
Messages
640
Reaction score
727
Location
SoCal
Website
www.linkedin.com
Vehicles
2023 F150 XLT PowerBoost 302A Avalanche BAP
Occupation
Engineer
Since owning my 2023 7.2kW PowerBoost, we have used it's incredible generator/inverter capability to power critical circuits in our house during multiple grid failures. Critical circuits include, refrigerator/freezers, furnace, security system, well pump and strategic lights and outlets. It has been flawless. The only problem has been grid failure when I am not home with the truck...duh! Soooo...

Of course, I could install a standby generator but that seems soooo 2010's. I have decided to build a battery backup system, with some twists.

System Requirements:

  • Easily power the critical circuits currently powered by PowerBoost.
  • Enough stored energy ( batteries ) to power critical circuits for three days.
  • Expandable energy storage
  • Include automatic transfer function <20ms - UPS mode - in grid down.
  • Include automatic transfer function to generator source ( PowerBoost ) to recharge batteries and power circuits

Simply put, I am building a home UPS system that will automatically recognize when either grid or PowerBoost is available to recharge batteries and power critical circuits. We rarely have grid failures over three days and with this system the PowerBoost should easily keep us going for weeks

Still in the planning stage, but very close to build stage. It should be fun!

Yes, of course, this offgrid design is most often used in solar or yacht systems, but I think the PowerBoost is the perfect secondary power source.

Here is a drawing of what I have come up with so far. I am NOT an electrician - obviously.

Oh, almost forgot! I did confirm a 30% Clean Energy tax credit for the system that can be carried forward until 2035. Cool!

backup-v3-5-to-scale.jpg
Careful, you may inspire me to spend money :)

I have been contemplating a similar application. We currently have battery (2x Powerwalls) backed solar with important loads on a subpanel. I suspect our current controller (Tesla?) may be able to determine when to use a) utility grid b) solar c) batteries and/or d) truck, truck playing the role of generator. If not, I am considering a transfer switch between the solar/batteries and the truck power. So, if grid is down and solar/batteries deplete the system could use truck power.

Please do keep us informed as to your progress with these Victrons, they might have a use in my application.

Anybody reading this know of anyone who has added truck/generator to a battery backed solar system?

Ford F-150 PowerBoost inspired hybrid house Screenshot_20241220_083739_Tesla
 

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
Have you considered an AIO? You haven't listed your loads, but it's not uncommon for a unit like this to run a whole home. They're also parallel capable and run in UPS mode. Adding solar is as simple as adding panels.
https://signaturesolar.com/eg4-flexboss21-16kw-ac-hybrid-inverter-48v-split-phase-21kw-pv-input/

If you want the gen input the other variant is what's needed (expect none of the units to work w/ the PB's GFI system)
https://signaturesolar.com/eg4-18kp...v-12lv-48v-split-phase-120-240vac-ul1741-cec/

They also have a smaller unit that puts you more in line w/ the pair of victrons
https://signaturesolar.com/eg4-12kp...t-phase-rsd-all-in-one-hybrid-solar-inverter/

Also, regardless of unit, be prepared to have to use a separate standalone charger that charges the batteries off of generator directly as the GFI of the PB may present a problem and trip its breaker.
https://signaturesolar.com/bigbatte...eatherproof-lithium-battery-charger-58-4v-dc/
 
Last edited:
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
Have you considered an AIO? You haven't listed your loads, but it's not uncommon for a unit like this to run a whole home. They're also parallel capable and run in UPS mode. Adding solar is as simple as adding panels.
https://signaturesolar.com/eg4-flexboss21-16kw-ac-hybrid-inverter-48v-split-phase-21kw-pv-input/
...
Thanks Hammaman.

Yes, I have looked at the Eg4 options. In fact the Eg4 LL batteries were my first choice - price/performance. Now the Pytes are gaining my support.

I am somewhat partial to Victron mainly because of their worldwide footprint and experience in offgrid and marine applications. I am a long since retired charter boat captain. I also have a couple of Victron components ( mppt charge controller and smart shunt ) in my travel trailer and will be upgrading to the Multiplus in the future. Other than that, I do agree that the Eg4 products do offer a lot for the money!

I am awaiting a response from Victron on the specific PB neutral-bonding GFI ground fault thing we have all experience and found workarounds for. I could tell you what I did for the last two years, but then I don't want to start another "one of those" threads.

Thanks again for the suggestions! I may be an old dog, but I can still learn new tricks!
 
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
Also, regardless of unit, be prepared to have to use a separate standalone charger that charges the batteries off of generator directly as the GFI of the PB may present a problem and trip its breaker.
https://signaturesolar.com/bigbatte...eatherproof-lithium-battery-charger-58-4v-dc/
My first answer from Victron:

The quattros have by default switching neutral ground switch.
When the quattro connect to the generator or your inverter that device should have the neutral ground bond.
The ground relays are programmable. I have included a Cerbo GX which gives remote access to the system for engineering support/monitoring. I'm feeling pretty good this will work. Yes, It's a bit of investment.
 
OP
OP
fwunder

fwunder

Well-known member
First Name
fred
Joined
Sep 1, 2022
Threads
23
Messages
224
Reaction score
357
Location
NJ
Vehicles
2023 F150 XLT 302A Sport 7.2Kw
Occupation
retired
@HammaMan

You should know I'm currently having lots of discussion with Victron experts. You may be correct with regard to the PB GFI issues. Trying to work it out but right now it is looking like the chargeverter option may make more sense. Might be a little less convenient, but I would save a little by going with split phase Multiplus instead of Quattro. And give me more generator options ( I have three ). Still digging!