Tonight power went out. I hooked up my truck as I have several times before. I have a certified power distribution panel.
Upon starting my truck, selecting power mode I'm getting all 240v on one leg and 0 on the other.
Unfortunately something has burned out in ny house because I smell burnt chips.
What would cause this?
Sponsored

 

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
Ooof -- that'd be the neutral not making contact. Yes, that will cook things as some devices could see over 200v while others only 40v.
 
OP
OP

Spiffy

Well-known member
First Name
Jeff
Joined
Jan 9, 2023
Threads
97
Messages
1,075
Reaction score
464
Location
Usa
Vehicles
2022 platinum powerboost
Occupation
Retired
Ya. Lost my washing machine control and my coffee machine. Not to bad this time.
2 years ago a storm caused the 18k feeder to short to one leg of my house feed. That caused extensive damage.

You mentioned neutral not making contact. Would that be somewhere in the truck or external?
I have current issues with my truck now. 12v state of charge, trailer brake module again. No interior lighting unless truck is on.
Like I mentioned b4 I haven't had this issue of 240 on one leg in the past.

Can you suggest diagnosis techniques?
 

Kanuck

Well-known member
First Name
Don
Joined
Aug 9, 2021
Threads
33
Messages
2,727
Reaction score
2,875
Location
Winnipeg, Manitoba
Vehicles
2021 XLT Scab 3.5 EB 6.5 Carbonized Grey Metallic
Occupation
Retired Electrician
Measure between neutral and each leg at the plug on the truck... should be 120 v on each leg to neutral.
Then at the end of the cord that connects to the house... should be the same.

If all reading correctly...problem is in the house.
 
OP
OP

Spiffy

Well-known member
First Name
Jeff
Joined
Jan 9, 2023
Threads
97
Messages
1,075
Reaction score
464
Location
Usa
Vehicles
2022 platinum powerboost
Occupation
Retired
I spent some time re reading the posts from the past. I kind of understood the bonded vs floating ground issue. Code and safety aside just for this subject I don't remember how my setup is.

Essentially here is what I do.

Flip main breaker off. disconnects from the feed.
Connect a 240v cable from my truck to a panel in the garage. 3 prong welder receptical. Garage is fed from main house panel.
Start truck and select generator mode. Flip 240v garage breaker on.
I know this is not the safe way.
It's worked fine in the past.
Should I remove the ground from the cable or not?

I have 120v on each leg on the truck now.
 

Sponsored

Kanuck

Well-known member
First Name
Don
Joined
Aug 9, 2021
Threads
33
Messages
2,727
Reaction score
2,875
Location
Winnipeg, Manitoba
Vehicles
2021 XLT Scab 3.5 EB 6.5 Carbonized Grey Metallic
Occupation
Retired Electrician
May have been a bad connection...
something not connecting ...
Hard to tell from a distance.
 

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
I spent some time re reading the posts from the past. I kind of understood the bonded vs floating ground issue. Code and safety aside just for this subject I don't remember how my setup is.

Essentially here is what I do.

Flip main breaker off. disconnects from the feed.
Connect a 240v cable from my truck to a panel in the garage. 3 prong welder receptical. Garage is fed from main house panel.
Start truck and select generator mode. Flip 240v garage breaker on.
I know this is not the safe way.
It's worked fine in the past.
Should I remove the ground from the cable or not?

I have 120v on each leg on the truck now.
A 240v 3 prong plug has no neutral -- I have no idea how you've wired it up.
 

scott011422

Well-known member
First Name
Scott
Joined
Feb 17, 2022
Threads
41
Messages
921
Reaction score
658
Location
60178
Vehicles
2022 F-150 Lariat 502a PB 7.2k 4x4 157"
Occupation
Engineer
Yeah, I'm not sure its even possible for the truck to give 240 on one leg. Each leg of 120v is from a separate inverter. I would lean on the house too.
 

dafish

Well-known member
Joined
Sep 11, 2023
Threads
22
Messages
354
Reaction score
219
Location
Midwest US
Vehicles
22 F-150 PB KR SCREW, '18 Lariat SCREW
Occupation
Mostly retired IT Pro - Cyber-IPT
A 240v 3 prong plug has no neutral -- I have no idea how you've wired it up.
Hamma, kind sir, that's not correct. The NEMA 6-30 is 2 hot legs and ground. The 14-30 is 2 hot legs and neutral, and the 14-30 is all 4.

Just sayin... :)
 

Sponsored


scott011422

Well-known member
First Name
Scott
Joined
Feb 17, 2022
Threads
41
Messages
921
Reaction score
658
Location
60178
Vehicles
2022 F-150 Lariat 502a PB 7.2k 4x4 157"
Occupation
Engineer
Hamma, kind sir, that's not correct. The NEMA 6-30 is 2 hot legs and ground. The 14-30 is 2 hot legs and neutral, and the 14-30 is all 4.

Just sayin... :)
14-30 is 2 hots 1 ground and 1 neutral.

10-30 and 10-50 dont have a ground.
 

powerboatr

Well-known member
First Name
Robert
Joined
May 9, 2022
Threads
173
Messages
4,343
Reaction score
5,427
Location
North East Texas, Piney Woods
Vehicles
2024 F250 King Ranch Chrome
Occupation
Retired Navy Senior Chief
Call an electrician
We had back feed a few years ago in the bus, when an inverter solenoid failed .we had 2 hots on each leg
Fried microwave, tv, clock and a couple feet of wire in the run to main panel and the cord .
Solenoid was to fail in only place coukd have ppwer it was a mess
We caught it in a few seconds..you know that death hum. Like a locked up motor followed by release of smoke.
Very lucky we got power killed fast

#8 wire melting is ugly
 
Last edited:

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
Call an electrical
We had back feed a few years ago in the bus, when an inverter solenoid failed .we had 2 hots on each leg
Fried microwave, tv, clock and a couple feet of wire in the run to main panel and the cord .
Solenoid was to fail in only place coukd have ppwer it was a mess
We caught it in a few seconds..you know that death hum. Like a locked up motor followed by release of smoke.
Very lucky we got power killed fast

#8 wire melting is ugly
Indeed, you can't put the magic smoke back into electronics. So easy to release it, impossible to put it back in.
 

dafish

Well-known member
Joined
Sep 11, 2023
Threads
22
Messages
354
Reaction score
219
Location
Midwest US
Vehicles
22 F-150 PB KR SCREW, '18 Lariat SCREW
Occupation
Mostly retired IT Pro - Cyber-IPT
Hamma, kind sir, that's not correct. The NEMA 6-30 is 2 hot legs and ground. The 10-30 is 2 hot legs and neutral, and the 14-30 is all 4.

Just sayin... :)
Argh... Typo above corrected. sigh..