What is the correct way to use your Pro Power to power a house through a 30A plug

mrichard02

Well-known member
Joined
Nov 27, 2024
Threads
22
Messages
55
Reaction score
13
Location
Massachusetts
Vehicles
2024 F150 Power Boost Lariat
Looking to see if anyone has a correctly diagramed solution for plugging in a PB to a house to power a house through a 30A plug.

And so that the PB doesn’t trip through its internal GFCI.
Sponsored

 

tsigwing

Well-known member
Joined
Oct 9, 2024
Threads
11
Messages
297
Reaction score
192
Location
DFW
Vehicles
2025 F150 PB
you need a transfer switch that switches the neutral and the hots
 

miniceptor86

Well-known member
First Name
Jim
Joined
Feb 13, 2025
Threads
2
Messages
93
Reaction score
104
Location
McGregor, iowa
Vehicles
2014 F150 FX4 Ecoboost, ‘25 powerboost on order, ‘39 Ford Tudor Standard
Occupation
tired
Best check with your electricity supplier. They will have an approved way to do this.
 

Sponsored

Severdog

Well-known member
First Name
Craig
Joined
Dec 20, 2021
Threads
27
Messages
410
Reaction score
539
Location
Landrum, SC
Vehicles
2022 F150 XLT Sport PB SuperCrew 6.5' 7.2Kw
Occupation
Trader
I am changing out my main panel to accomplish this. You need to separate your neutrals and grounds on all circuits run to the panel, i.e. make the panel into a common "subpanel." This also implies that your neutral/ground bond is at the service entrance. Or you can cheat like many do and just cut the ground lead of the umbilical cord to prevent GFCI fault, since there is now no "double path" back through ground or neutral.

You can backfeed the PPO though a breaker at the top of the panel that has an interlock with the panel shutoff.

I plan to document this job with a video once I can get Duke Power to cut over from my old outside panel to the new one.
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
I am changing out my main panel to accomplish this. You need to separate your neutrals and grounds on all circuits run to the panel, i.e. make the panel into a common "subpanel." This also implies that your neutral/ground bond is at the service entrance. Or you can cheat like many do and just cut the ground lead of the umbilical cord to prevent GFCI fault, since there is now no "double path" back through ground or neutral.

You can backfeed the PPO though a breaker at the top of the panel that has an interlock with the panel shutoff.

I plan to document this job with a video once I can get Duke Power to cut over from my old outside panel to the new one.
Don’t do this! The only correct way, according to the National Electrical Code, is to use a Neutral Switching Transfer switch, (3poles instead of 2).
https://www.generacpowerproducts.co...ac-HomeLink-Manual-Transfer-Switch/p/G0068541
Code allows for only one grounding source on a service To ensure that your breakers will trip during a short circuit to ground.
 

Lefty665

Well-known member
First Name
Cliff
Joined
Nov 25, 2024
Threads
3
Messages
99
Reaction score
69
Location
Beaverdam, Va
Vehicles
2024 F150 XLT Powerboost Antimatter Blue, '98 Mustang GT, '64 Olds 442
Occupation
retired IT
3 wires from PB to house panel. 2 hots and a neutral will prevent ground faults. An auto interlock to prevent back feed to the line will make you much more popular with your local linemen and power company. A sub panel (commonly bundled with interlocks) with circuits you want powered by PB and which will not have demand exceeding 7.2kw total, or 3.6kw per leg will make for a happier experience.

For the OP who was either unwilling or unable to search the forum for several extensive threads on using PB to power a house the answer is call an electrician and get out your checkbook.

Tks to a couple of you who have provided links to those threads. (y)
 