Not at all. I think there is a little something in his solar configuration that cause the problem with the 7.2KW. As you stated probaly the provider of his solar system might be able to help him. I had a proper panel installed for my house and I run most of my electrical except for oven/dryer and few plugs. I love my 7.2kw and the truck that came with it :)
Ahhhh. OK.

I'm certainly not an electrician, but I find it intriguing to consider designing an off-grid solar/battery dwelling with the Powerboost as a second source. I figured without the complexity of grid power and the danger of feeding the grid unintentionally, that there would be more options. In fact, couldn't it be designed similar to an RV with solar and big batteries?
Sponsored

 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
The reason you need the proper transfer switch is to isolate your solar power system from the truck When it is suppling power.

do not listen to anyone telling you to lift the bond on the truck!!! The ground fault system is there to protect you. This removes the protection.

you will need a Reliance XSeries or Generac 6852. I don’t know how your inverter is feeding your 120/240v appliances or how the generator is tied in to feed the batteries. I highly suggest bringing a licensed electrician out to install this for you
 

jeffcrum

Well-known member
First Name
Jeff
Joined
Feb 21, 2021
Threads
2
Messages
652
Reaction score
698
Location
Lake Saint Louis, MO
Vehicles
2021 F-150 XLT 302A Powerboost 7.2kw Inverter
Occupation
Computer programmer
No way you need a transfer switch. Nothing against @Hullguy. I am very impressed with his electrical knowledge.

But, @Snakebitten has the right path here. Your setup should work just like an RV with solar and batteries that can also plug into shore power!
 

Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
Ahhhh. OK.

I'm certainly not an electrician, but I find it intriguing to consider designing an off-grid solar/battery dwelling with the Powerboost as a second source. I figured without the complexity of grid power and the danger of feeding the grid unintentionally, that there would be more options. In fact, couldn't it be designed similar to an RV with solar and big batteries?
Potentially but I don't have a clue about the electrical design of a RV
 

daemonic3

Well-known member
First Name
Terry
Joined
Sep 22, 2020
Threads
22
Messages
1,808
Reaction score
1,750
Location
Sacramento, CA
Vehicles
2017 F150 3.5EB
Occupation
Engineer
Hello,

I've been loooking around the forums and see some discussion about powering a home with the ProPower, the need for a transfer switch, etc. I have an off grid cabin with a solar system and am wondering if there are some cheaper/easier options for me since I'm not connected to the grid? I have a 30A 240V plug that I typically plug into a generator to charge my solar batteries/run the cabin. It faults immediately when I plug into my ProPower.

I've read that I can remove the ground from my cable that goes truck to the solar inverter inside the cabin but not safe. I appreciate any comments/help with this. Thanks.
What's intruiging to me here with all the talk of transfer switches and isolation from the solar in order to use the propower... is that he ALREADY has a system designed to have an external generator as a 2nd source to charge the batteries and run the cabin. I feel like this got overlooked somehow?

What it *sounds* like to me is that his existing generator is a floating neutral and the propower is known to be bonded neutral. The propower is likely throwing the ground fault because of the double bonding (truck and home). Since his house and solar are already designed to have this external generator connection without additional isolation, wouldn't he only need to "transfer" his neutral over from the home bond to the truck bond?

Not trying to argue just trying to learn from the experts here.
 

Sponsored

Atlee

Well-known member
First Name
Erroll
Joined
Sep 14, 2021
Threads
27
Messages
1,282
Reaction score
1,314
Location
Mechanicsville, Virginia
Vehicles
2022 Power Boost, XLT 302A, 4x4, SCrew, 6.5' bed
Occupation
retired
The reason you need the proper transfer switch is to isolate your solar power system from the truck When it is suppling power.

do not listen to anyone telling you to lift the bond on the truck!!! The ground fault system is there to protect you. This removes the protection.

you will need a Reliance XSeries or Generac 6852. I don’t know how your inverter is feeding your 120/240v appliances or how the generator is tied in to feed the batteries. I highly suggest bringing a licensed electrician out to install this for you
A transfer switch similar to a Class A or Class B or Class C. All 3 of those have an automatic transfer switch which automatically switches from on board generator and shore power, dependinf on the source of electricity.
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
7
Messages
488
Reaction score
468
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
The reason you need the proper transfer switch is to isolate your solar power system from the truck When it is suppling power.

do not listen to anyone telling you to lift the bond on the truck!!! The ground fault system is there to protect you. This removes the protection.

you will need a Reliance XSeries or Generac 6852. I don’t know how your inverter is feeding your 120/240v appliances or how the generator is tied in to feed the batteries. I highly suggest bringing a licensed electrician out to install this for you
Not to be argumentative, but to state how I see it.
the current off grid system has it’s own existing grounding/bonding system. When you introduce the Powerboost you add a second grounding/bonding system. The Powerboost “sees” the off grid bonding system and goes into fault. This is why I feel you do need the transfer switch.
 

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
The issue here is that there is a ground inside the house that the truck is sensing. Since the house is not grid connected there is no need for the transfer switch. I suspect the simplest solution would be to disconnect (eg open the breaker) the solar system when using the truck.
 

jeffcrum

Well-known member
First Name
Jeff
Joined
Feb 21, 2021
Threads
2
Messages
652
Reaction score
698
Location
Lake Saint Louis, MO
Vehicles
2021 F-150 XLT 302A Powerboost 7.2kw Inverter
Occupation
Computer programmer
So, we aren't talking about switching from generator to shore power. He is using a generator as shore power.

The 'shore power' should take in a bonded neutral/ground just fine.

There is something not wired correctly with the charge controller.
 

daemonic3

Well-known member
First Name
Terry
Joined
Sep 22, 2020
Threads
22
Messages
1,808
Reaction score
1,750
Location
Sacramento, CA
Vehicles
2017 F150 3.5EB
Occupation
Engineer
So, we aren't talking about switching from generator to shore power. He is using a generator as shore power.

The 'shore power' should take in a bonded neutral/ground just fine.

There is something not wired correctly with the charge controller.
This is why I'm so confused. The battery charge controller is already seemingly designed to have 2 sources (generator and solar) to manage itself. I don't know why a portable genny would not need a transfer switch while a propower genny would require it (as suggested by others here) unless it is strictly for that neutral.

Curious why 'shore power' should be able to take in a bonded neutral ground though? I've read elsewhere (probably on this forum) how you can't have the neutral bond in 2 places. I thought that was part of what the grid-based home transfer switches do - switch the hots and neutral to the propower.

Perhaps I'm just way lost and confused.
 

Sponsored


Yves

Well-known member
First Name
Yves
Joined
Jun 12, 2022
Threads
1
Messages
157
Reaction score
109
Location
Gatineau, Quebec, Canada
Vehicles
F-150 2021 Powerboost XLT 302A 360 Camera 7.2KW
Occupation
Retired
@OT66 do you have information than you can provide about your current configuration? We are guessing solutions/options for you but we don't have a clue about your configuration.....
 
OP
OP

OT66

Active member
Joined
Sep 5, 2022
Threads
1
Messages
30
Reaction score
9
Location
Ontario, Canada
Vehicles
F150 Powerboost
@OT66 do you have information than you can provide about your current configuration? We are guessing solutions/options for you but we don't have a clue about your configuration.....
I'll give as much info. as I can. I have a L14-30 male plug outside that for years has plugged into a portable generator/inverter. That goes to my Magnum inverter (MS 4024 PAE). When I turn on the generator it will charge the battery bank and it also powers the cabin at the same time. When the generator is turned off it runs off of battery/solar. I have a 60 amp electrical panel that the Magnum inverter is connected to. This system was already in place when I got the cabin, so if I'm not providing enough info. I apologize.
 

Snakebitten

Well-known member
First Name
Bruce
Joined
Jun 19, 2021
Threads
5
Messages
11,560
Reaction score
22,964
Location
Coastal Texas
Vehicles
2022 F150 KingRanch Powerboost
Just curious....
What portable generator have you used successfully? And did it come with the cabin or did you bring it?

I'm envious of your cabin! :)
 

Gros Ventre

Well-known member
First Name
Bill
Joined
Nov 13, 2021
Threads
47
Messages
2,690
Reaction score
1,815
Location
Western Wyoming
Vehicles
Powerboost
Where is your ground in the cabin? The cause of the shutdwon of your truck is that it's sensing a ground other than its own neutral ground bond. Second item: can you find out if the generator you've been using is a floating neutral or a bonded neutral?
 

daemonic3

Well-known member
First Name
Terry
Joined
Sep 22, 2020
Threads
22
Messages
1,808
Reaction score
1,750
Location
Sacramento, CA
Vehicles
2017 F150 3.5EB
Occupation
Engineer
I'll give as much info. as I can. I have a L14-30 male plug outside that for years has plugged into a portable generator/inverter. That goes to my Magnum inverter (MS 4024 PAE). When I turn on the generator it will charge the battery bank and it also powers the cabin at the same time. When the generator is turned off it runs off of battery/solar. I have a 60 amp electrical panel that the Magnum inverter is connected to. This system was already in place when I got the cabin, so if I'm not providing enough info. I apologize.
Fascinating! That inverter seems to (from the product page) only take in 24V DC. I don't see a "bypass mode" where it can take in a generator 240V AC and pass it through on its outputs. So now I have no idea where that male cord taps into your existing system.

Maybe you have a 2nd AC->DC converter on the genny input directly to the battery bank charger, so when running off genny you are actually charging the battery and running off battery, effectively going AC->DC->AC again? If so that is very lossy, but it does allow you to charge the battery bank. The more efficient way would be a bypass of the battery and you put a transfer switch between the inverter and panel, because your inverter is effectively your "grid" in this house. You'd lose the ability to charge the battery in that case.

Again, I defer to the experts here but this is a very interesting saga!