Ok, I’m starting a new thread partly because I’m dense and partly because the mega thread on using the propower with a transfer switch has just gotten too mega. I figured titling my thread with my equipment could possibly help somebody in the future.
So here’s the deal. My transfer panel is arranged to switch the hots from either each individual circuit on the main panel OR one of the two hot legs from the generator leg. Incoming from the generator will be two hots, neutral and ground. Both neutral and ground are setup to connect directly to the main panel (bypassing the transfer switch, although the sub panel chassis will be grounded). The house is bonded neutral and ground.
The bonded neutral ground dilemma is just not sinking in to my thick head. When I start flipping the transfers from main to gen, am I going to have faults? And if so, how do I fix this? Hope this works because the equipment is purchased and half installed.

https://www.reliancecontrols.com/pr...-2-1p-20a-6-1p-15a-circuits-metal-gray-310cdk

This image shows the wiring available.

Ford F-150 Propower to Reliance 310C CF536350-6E7A-43A0-9C46-67C8436CBD16


Ford F-150 Propower to Reliance 310C 57F7DCF7-EF5F-48CF-B82C-610F13E60CBA
Sponsored

 

na8rboy

Active member
First Name
Mark
Joined
Nov 26, 2023
Threads
0
Messages
34
Reaction score
11
Location
Northern WI
Vehicles
23 powerboost lariat fx4
Occupation
GC
You need a 3 pole transfer switch (GFI) If your going to use a transfer switch. There is other ways around it but. They are frowned apon.
 

na8rboy

Active member
First Name
Mark
Joined
Nov 26, 2023
Threads
0
Messages
34
Reaction score
11
Location
Northern WI
Vehicles
23 powerboost lariat fx4
Occupation
GC
Which is a neutral transfer switching.
 
OP
OP
BUDXR7

BUDXR7

Well-known member
Joined
Nov 19, 2023
Threads
6
Messages
113
Reaction score
111
Location
Massachusetts
Vehicles
2023 XLT 302A PB SCREW 4X4
I don’t follow. This sub panel doesn’t even have provisions for neutral connection. It is designed to just pas the generator neutral thru to the main panel.
 

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
Where is your cable running to? What's the generator interconnect point? The whole neutral through the panel is a little odd sounding as per code the grounds and neutrals should be run together in the same run. Can you map out your entire panel assembly? I'm not familiar with this device itself and the wiring underneath looks a little strange. Diagrams help out considerably.
 

Sponsored

OP
OP
BUDXR7

BUDXR7

Well-known member
Joined
Nov 19, 2023
Threads
6
Messages
113
Reaction score
111
Location
Massachusetts
Vehicles
2023 XLT 302A PB SCREW 4X4
Not sure if this will help - forgive how amateurish this is. For simplicity I’m only depicting 1 circuit on each phase (the sub panel has 10 total circuits). “T” is transfer, each circuit has its own switch. “B” is the corresponding breaker. They way it’s wired; remove hot from original breaker in the main panel. Run a jumper from that breaker to a corresponding transfer switch in the sub panel. That transfer switch then feeds a secondary breaker (yes, all these circuits end up with redundant breakers). Then from there you run another jumper back to the main panel and wire nut to the load. All the jumpers are pre wired in the bundle that you see hanging from the sub panel. So the intent of the manufacturer (I think) is to connect each phase from the generator to “a” and “b” bus in sub panel (these are the 10 gauge loose red and black wires you see in the sub panel) then send the neutral (you can see a 10 gauge white wire in the bundle of jumpers to the main panel) and ground from the generator right over to the bonded bus in the main panel.
Ford F-150 Propower to Reliance 310C 6F1C2041-9C79-4079-BBC7-BB3415A803DC
 

madsend81

Well-known member
Joined
Aug 30, 2023
Threads
13
Messages
197
Reaction score
352
Location
East San Diego County, CA
Vehicles
2023 F150 PB XLT Sport 4x4, 157" WB
Occupation
Engineer
That setup isn't going to work with the ProPower on the PB. You need to switch the neutral as well as legs. See attached sketch that I quickly drew up. Top is a typical house setup. Bottom shows how the transfer switch needs to be incorporated. I left out details on the breaker panel for simplicity's sake.

Ford F-150 Propower to Reliance 310C IMG_20231213_211949452
 

na8rboy

Active member
First Name
Mark
Joined
Nov 26, 2023
Threads
0
Messages
34
Reaction score
11
Location
Northern WI
Vehicles
23 powerboost lariat fx4
Occupation
GC
I don’t follow. This sub panel doesn’t even have provisions for neutral connection. It is designed to just pas the generator neutral thru to the main panel.
Your neutral and grounds are bonded in main panel. It will trip trucks breaker.
 
OP
OP
BUDXR7

BUDXR7

Well-known member
Joined
Nov 19, 2023
Threads
6
Messages
113
Reaction score
111
Location
Massachusetts
Vehicles
2023 XLT 302A PB SCREW 4X4
I understand this. I see the generac 6852, which switches the neutral, will resolve this. It’s the only generator sub panel I see that will do this though. If all modern generators are going to be neutral bonded I don’t understand why they manufacture these panels that only switch the hots. Seems that would have a very limited market to sell them into.
 

na8rboy

Active member
First Name
Mark
Joined
Nov 26, 2023
Threads
0
Messages
34
Reaction score
11
Location
Northern WI
Vehicles
23 powerboost lariat fx4
Occupation
GC
I understand this. I see the generac 6852, which switches the neutral, will resolve this. It’s the only generator sub panel I see that will do this though. If all modern generators are going to be neutral bonded I don’t understand why they manufacture these panels that only switch the hots. Seems that would have a very limited market to sell them into.
A portable generator will work with your current setup, but truck won't. There's two types bonded and Floating.
 

Sponsored


na8rboy

Active member
First Name
Mark
Joined
Nov 26, 2023
Threads
0
Messages
34
Reaction score
11
Location
Northern WI
Vehicles
23 powerboost lariat fx4
Occupation
GC
Most portable generators are floating neutrals. Truck is bonded.
 

HammaMan

Well-known member
Joined
Sep 7, 2022
Threads
123
Messages
8,526
Reaction score
9,934
Location
SE US
Vehicles
2022 307a PB
Most portable generators are floating neutrals. Truck is bonded.
Most portables are neutral bonded. They work because they don't have GFI breakers on the 30a connector, if they even contain GFI breakers.