This is becoming overly complicate! It all comes down to the off the grid systems ground and the Powerboost adding a second ground!
The installation manual, (https://www.magnum-dimensions.com/file/2414/download?token=jvCyRGs3), page 13, shows the grounds from the batteries, solar arrays, and AC source having all the grounds landed together!
This becomes the same issue as trying to use the Powerboost to power a on the grid house! You need a neutral switching transfer switch!
The inverters OT66 was using set all floating grounds. Which is why they worked.
Once again, I highly recommend NOT using a device to lift the Powerboost ground. You are defeating the safety’s if you do so
The installation manual, (https://www.magnum-dimensions.com/file/2414/download?token=jvCyRGs3), page 13, shows the grounds from the batteries, solar arrays, and AC source having all the grounds landed together!
This becomes the same issue as trying to use the Powerboost to power a on the grid house! You need a neutral switching transfer switch!
The inverters OT66 was using set all floating grounds. Which is why they worked.
Once again, I highly recommend NOT using a device to lift the Powerboost ground. You are defeating the safety’s if you do so