Regarding strange voltages without a ground present, I'm not seeing how that would happen with these trucks unless something else is off with the building its being connected to. These trucks are designed to power devices plugged into them, which have no ground rod present, so this shouldn't be...
By taking the ground out at the plug, he hasn't removed the ground from the houses electrical system. It is still grounded via the ground rod that should be installed already at the meter. The truck never had a ground, and by taking it out at the plug, it still doesn't. I really don't see the...
In regards to the "interlock method" a lot has been said about how disconnecting the ground wire between the panel and the PB generator isn't up to code. While I believe that is true, there has to be a reason. I'm just struggling to figure out what that reason is.
Something to consider that I...