OK so we know that not grounding the plug between house and truck is a bad idea, but in practice has been proven that it can power an interlock. Tieing the ground to the neutral at the truck side of the plug should similarly have the same result and provide a 'valid' ground path from the...
Sorry, I should have been more specific. You had referred to a neutral switching transfer switch, and I took your meaning to be that there is a potential way to perform the neutral/ground separation that would be required in a way that could be done in a whole house/interlock capacity...
Could you provide an example of what this would look like? Can you recommend a product that would fit the intended way you're recommending I think about solving the need?
Thanks
Could that be done in a way that would still allow a whole home setup or would I then be back to picking specific circuits? If i do a transfer switch to backfeed into the whole panel, would I then be tied into using a bonded neutral generator due to the initial considerations to make the truck...
All,
Just recently purchased a F150 Platinum with the 7.2kw PPO option with the intention of being able to use it to power the house in case of outages then found all of the info related to the potential issues associated with using an interlock setup due to the bonded neutral configuration our...